-Dan
Moderator: 3liteguy
RunsWithCrouse-Hinds wrote:New Idea!: Use overlap-by-phase up such that phase 2 consists of phase 2 and 9, and phase 6 consists of phase 6 and 10. THEN, set OLA and OLB to flash green, and assign OLA to phase 9, and OLB to phase 10. THEN, under normal operation, FYA will work as expected, and when you want protected ONLY, you can OMIT phase 9 or 10. Brilliant? I think so! Hope it actually works, someone should try it out!
-Dan
sorphin wrote:Dan B,
0x09 the last 4 bits are for 1hz flashing overlaps.
RunsWithCrouse-Hinds wrote:sorphin wrote:Dan B,
0x09 the last 4 bits are for 1hz flashing overlaps.
Hmm, didn't notice that in the document, but whatever. And by "last 4 bits", do they/you mean 8, 2, 4, and 1, or 16, 32, 64, and 128 (in terms of binary)? I haven't been quite sure which direction the Econolite write-protect stuff goes. So basically, 00001111 for all flashing greens, or 11110000?
-Dan
0x009 Controller
Maryland fast flash (5 Hz) on overlap A on a per phase basis.
Overlap “A” green will flash @ 5 Hz when it is green during the following programmed phases.
Bit 0 = Phase 9
1 = Phase 10
2 = Phase 11
3 = Phase 12
Bits 4 - 7 are used to flash the standard overlap greens at the
rate of one hertz
Bit 4 = Overlap A (flash the OLA green at the 1 PPS)
5 = Overlap B (flash the OLB green at the 1 PPS)
6 = Overlap C (flash the OLC green at the 1 PPS)
7 = Overlap D (flash the OLD green at the 1 PPS)
sorphin wrote:So i tested your FYA setup finally last night... Found some issues..
It works.. -if- you have 1 FYA... but not if you have a pair, like you'd normally see..
I have 1/6 and 2/5.
if i set it up the way you say, when 5 goes protected, the FYA on 1 turns off and the light is red. and vise versa. So far, no tweaking of protected/permissive fixes that.
coyttl wrote:sorphin wrote:So i tested your FYA setup finally last night... Found some issues..
It works.. -if- you have 1 FYA... but not if you have a pair, like you'd normally see..
I have 1/6 and 2/5.
if i set it up the way you say, when 5 goes protected, the FYA on 1 turns off and the light is red. and vise versa. So far, no tweaking of protected/permissive fixes that.
.. I'm confused. All the FYA's I've seen, if the thru (6) has to turn red because the opposing left (5) goes green, the close left (1) will go red as well.
Is this not how it a FYA is supposed to act?
--Mike.
sorphin wrote:All the FYAs around here... least that i've seen (and hence how my original setup works)...
You have protected green on 5... the FYA on 1 is well... flashing yellow arrowing.
You have protected green on 1... the FYA on 5 is well... flashing yellow arrowing.
coyttl wrote:sorphin wrote:All the FYAs around here... least that i've seen (and hence how my original setup works)...
You have protected green on 5... the FYA on 1 is well... flashing yellow arrowing.
You have protected green on 1... the FYA on 5 is well... flashing yellow arrowing.
I tried this last night -
I do not get this. I get 'normal' behaviour:
Say both 2 & 6 thrus were being serviced, rest in green. Phases 5 and 1 are FYA.
I place a call on phase 1.
Phases 2 and 5 go yellow, then red. Phase 1 stays FYA.
Phase 1 goes green.
Phase 1 then goes yellow, then red.
Phase 2 goes green, phase 5 goes FYA, phase 1 goes FYA.
From looking at your result, I think you have two phases crossed -
In the overlap screen for 'A' (which is phase 1 above, concurrent with 6), it needs to have PROTECTED for phase '1' and PERMISSIVE for phase '6', not 2.
Ini the overlap screen for 'B' (which is phase 5 above, concurrent with 2), it needs to have PROTECTED for phase '2', and PERMISSIVE for phase '5', not 1.
--Mike.
Users browsing this forum: SignalFreak and 0 guests